KVAr
Posts: 346
Registered: 7/13/07
Re: Smart UPS 1500 buzzing like crazy
Posted: Jul 13, 2007 1:52 PM in response to: nicolen
Reply
Asymmetry in the line voltage will cause any transformer to buzz like crazy and anything with a half wave rectifier will do just that. Since the Smart-UPS has a rather large transformer, the effect will be very noticeable. Two step lamp dimmer, overhead projector and hair dryers are notorious for that. If there are overhead projectors or two-step lamp dimmers, try turning them all off. If this doesn't apply to you, have an electrician come out to test your power line for 2nd, 4th and 6th harmonics.
If you don't have anything like that in your building, then it is possible that someone has a three phase motor drive with a failed component causing a DC offset on your line.
This goes for you too nicolen. I did notice your profile say you're on behalf of "CK Manufacturing and Trading, Inc.". Perhaps you have some large VFD motor drives within the building.
Message was edited by: KVAr